604 battery abnormal mode code

Any help would be appreciated. We have recently been getting a 604 error code on our ZAMP Solar controller when we use the electric BUN coffee maker (1300w). We've owned the SMB since it was new in 2015. We've had the coffee maker for the same time. We had 2 new house AGM batteries installed fall of 2018. (May be unrelated to the issue).

The 604 code states that this is an overheating indicator. The digital themperature readout on the ZAMP goes from 29C to 65C when making a cup of coffee. So it does seem to be overheating. The 604 popped on when the temp hit 65C. We're just not sure why its overheating. The inverter fan came on at about 45C.

We have a goucho couch along the driver side of the van. The Magnun MS2000 inverter is mounted under the couch. We have 2 new house batteries and 2 solar panels.This issue happens even we've been fulled topped off by shore power.

Thoughts??
__________________

bglockwood is offline   Reply With Quote
Old 07-13-2019, 09:46 PM   #2
Senior Member
 
Scalf77's Avatar
 
Join Date: May 2007
Location: Beaverton, OR
Posts: 1,441
It would appear that your battery or battery sensor is getting hot, which throws the code. I would expect the temperature gain is from using your magnum inverter. Have you checked what the temperature reading is on the magnum controller.

-greg
__________________

__________________
2004 E350 EB V10 E/PH 2WD
Scalf77 is offline   Reply With Quote
Old 07-14-2019, 06:44 AM   #3
Member
 
Join Date: Dec 2015
Posts: 66
This could be as simple as a bad connection. Where, exactly, is the temperature sensor that is going over-temp? If it is bolted to the battery minus, as some I've seen, it may be that the battery minus connection is a bit corroded or simply loose, and presenting a high resistance. Under normal charging, especially from solar, the currents are relatively low, and so the I2R heating is low. You start pulling 100A to run your coffee maker through the inverter, and the I2R heating goes through the roof.
Try checking all your connections, especially any around the temperature sensor.
Wowbagger is offline   Reply With Quote
Old 07-14-2019, 11:14 AM   #4
Junior Member
 
Join Date: Sep 2014
Location: Arizona
Posts: 8
604 code

Thank you for your replys. We took the seat off the goucho and created a makeshift fan to blow more air across the inverter. (Picture attached for your amusement). This did seem to keep it cooler, but still not a solution. We determined/confirmed that this 604 code does not occur if we're on shore power (ie using DC; not going thru the inverter).

As this issue did not occur until we had the new house batteries installed (by CamperWorld Tempe, AZ), our next step is going to be to drop the batteries and check all the connections. We told camperworld that we wanted to replace the batteries with the exact same batteries as we had from Sportsmobile. They ended up with something a little different; which then required different battery connectors than the ones we had (either we hand "L" connectors and they put a different connector on or the other way around. I don't recall.) Again, this makes us suspicious of the connections.

As we're in Minnesota right now, we're going to take it to a shop we trust to drop the batteries and check connections.

Any additional thoughts anyone has will be much appreciated.

FYI- the inverter manual states that the inverter environmental temp should be less than 77F. Not sure how that's even possible in many instances with the inverter mounted below the goucho, and we camp in the desert SW a lot.
Attached Thumbnails
20190713_161916.jpg  
bglockwood is offline   Reply With Quote
Old 07-14-2019, 12:30 PM   #5
Member
 
Join Date: Dec 2015
Posts: 66
I think you will find that temperature is 77C, not 77F.
Wowbagger is offline   Reply With Quote
Old 07-14-2019, 02:15 PM   #6
Junior Member
 
Join Date: Sep 2014
Location: Arizona
Posts: 8
77C does make more sense. I'll look at the book again.
bglockwood is offline   Reply With Quote
Old 07-15-2019, 06:35 AM   #7
Senior Member
 
Scalf77's Avatar
 
Join Date: May 2007
Location: Beaverton, OR
Posts: 1,441
I believe the high temp shutdown for the inverter/charger is 54C. The 77F is the standard temp-voltage setpoints, As the battery temperature goes up or down, the temp sensor compensates the output voltage. You would normally trip internal FET or Transformer Temp sensors on the magnum before a battery temp issue.

The magnum sensor is a little slower to react then some others, so the question would be you actually trip the inverter or are you just getting the 604 code on the solar charger.

I agree that your best action is to drop the batteries and look at the connections. I have seen a couple of sensors that can be put on the positive post but most have to go on the negative.

-greg
__________________

__________________
2004 E350 EB V10 E/PH 2WD
Scalf77 is offline   Reply With Quote
Reply

Tags
604, inverter, overheating

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Sportsmobile SIP or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 06:21 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.