Somewhat scary solar meltdown

...So I noticed that my house batteries weren't charging today......

I have 320W of solar on the roof wired in parallel, and run 10AWG wire from the panels to a Blue Sea fuse block (positive only) through a 25A fuse and on to the solar controller.

Here's what the fuse block looks like today:








......and here's the wire termination from the panels to the fuse block...




After an extensive post-meltdown forensic analysis (come on.....really??....), my conclusions are either:

I didn't tighten the fuse block terminal screw sufficiently and the contact resistance at the screw terminal created enough heat to melt the fuse block

or

The screw was sufficiently tight, but the thermal cycling of pumping 16A thru the terminal at high noon and cooling everything off at midnight slowly worked the screw loose.....increasing contact resistance at the screw enough to melt plastic.



...just happy my van didn't burst into flames.....

__________________
2008 E350 RB passenger 4WD SMB penthouse
2013 KTM 350 EXC
2008 KTM 250 XCF-W
2003 Honda Element
boywonder is offline   Reply With Quote
Old 09-10-2016, 05:55 PM   #2
Senior Member
 
Join Date: Apr 2014
Location: Poughkeepsie, New York
Posts: 122
You can make a lot of heat with 20 amps. It reminds me of my 30 amp 110 inlet plug meltdown. We were both lucky that there was no fire.
__________________
2015 Promaster Sportsmobile
KB2ZE
Old retired IBM Engineer
DCHitt is offline   Reply With Quote
Old 09-10-2016, 06:56 PM   #3
Senior Member
 
Flux's Avatar
 
Join Date: Aug 2016
Location: Reno, NV
Posts: 1,420
No fuse between the controller and the distribution panel??

I'm a bit confused as to how a loose contact did this without some sort of short to ground. I'm not an electrical wiz though, but I got the basics. Seems like it had to arc to something right?? Almost looks like it arced to the top of that 25 amp blade fuse.

I was reading up on those blade fuses and they are not exactly quick acting. They can draw overcurrent for minutes at a time.

I am very glad your damage was minimal. Yikes!!

EDIT: I get it now, there was some current draw on the other side, loose connection turns into a resistance heater.

Yikes again.
Flux is offline   Reply With Quote
Old 09-10-2016, 07:06 PM   #4
Senior Member
 
ShuttlePilot's Avatar
 
Join Date: Aug 2012
Posts: 632
Greetings Boywonder, first, just want to say how I'm relieved something worse didn't happen. Second, that amount of amps is a lot to ask from a spade connector to handle. I would recommend a cable lug terminal for for anything north of 10 amps. If there is any consolation to this is you might have just found a point of high resistance that's been robing a chunk of your solar power.

-Eric
__________________
2005 SMB RB 4x4 6.0 PSD
A rocket on the pad is safe,
but it's not what rockets are built for.
ShuttlePilot is offline   Reply With Quote
Old 09-10-2016, 08:29 PM   #5
Senior Member
 
Scalf77's Avatar
 
Join Date: May 2007
Location: Beaverton, OR
Posts: 2,490
Quote:
Originally Posted by ShuttlePilot View Post
Greetings Boywonder, first, just want to say how I'm relieved something worse didn't happen. Second, that amount of amps is a lot to ask from a spade connector to handle. I would recommend a cable lug terminal for for anything north of 10 amps. If there is any consolation to this is you might have just found a point of high resistance that's been robing a chunk of your solar power.

-Eric
ditto, also it looks like in effect your are terminating to the fuse on the fuse panel. This also increases heat in the area. Do you also have it fused at the controller?

-greg
__________________
-greg
__________________________________________________ ______________
"Goldilocks" 2020 Ford Transit High Roof Extended 3.5 EcoBoost AWD Homebuilt
Scalf77 is offline   Reply With Quote
Old 09-10-2016, 09:59 PM   #6
Senior Member
 
rallypanam's Avatar
 
Join Date: Feb 2013
Location: San Francisco/Nevada City
Posts: 3,769
Yikes! Glad it wasn't worse!

I'm trying to remember how I did mine.. I think controller to battery is like 6 gauge through a big car stereo fuse, but I don't remember off the top of my head.
rallypanam is offline   Reply With Quote
Old 09-11-2016, 01:50 PM   #7
Senior Member
 
boywonder's Avatar
 
Join Date: Jul 2013
Location: So Cal
Posts: 4,045
Quote:
Originally Posted by Scalf77 View Post
ditto, also it looks like in effect your are terminating to the fuse on the fuse panel. This also increases heat in the area. Do you also have it fused at the controller?

-greg
....not sure what you mean by terminating to the fuse on the fuse panel....

The controller is about 2 feet away...this is the fuse from the panels....the fuse between the controller and house batteries is about 2 inches from the controller.....a different Blue Sea 6 circuit with ground buss.

.....thinking about using an in-line ATO fuse holder with butt-splices to eliminate the screw terminals.............
__________________
2008 E350 RB passenger 4WD SMB penthouse
2013 KTM 350 EXC
2008 KTM 250 XCF-W
2003 Honda Element
boywonder is offline   Reply With Quote
Old 09-11-2016, 02:10 PM   #8
Senior Member
 
rallypanam's Avatar
 
Join Date: Feb 2013
Location: San Francisco/Nevada City
Posts: 3,769
Oh, so this is fuse between panels and controller.. I get it now, higher amps. I don't think I have a fuse... just straight from panels to controller, I think that's the way Blue Sky recommended. Is that bad?
rallypanam is offline   Reply With Quote
Old 09-11-2016, 02:28 PM   #9
Senior Member
 
gcvt's Avatar
 
Join Date: Jul 2014
Location: Longwood, FL
Posts: 1,560
^ I'm wondering the same thing as I gather components for my upcoming solar install.
__________________
Greg
Old van: 1997 E250 EB30 (Stolen)
New van: 2003 E250 EB10
gcvt is offline   Reply With Quote
Old 09-11-2016, 02:41 PM   #10
Senior Member
 
MadScience's Avatar
 
Join Date: Jul 2011
Location: SF Peninsula
Posts: 809
I don't have a fuse there either. Wondering as well now.

At some point there was a very large batch of bad automotive blade fuses that went into circulation; they would cook rather than blow. Might be worth testing one of the others and replacing them all if it behaves that way.
__________________

'99 EB ex ENG KSWB news van, low rent 4x4 conversion (mostly fixed by now), home built interior.
MadScience is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off