Replacement GFI Amps

When we had a pre-purchase RV inspection done the GFI kept tripping. We were told to replace the old GFI with a new 20A GFI outlet, even though the GFI Breaker is only 15Amp. Help me understand that? Should the new GFI be only 15A - the same as the breaker or does it matter?

rtamobile is offline   Reply With Quote
Old 05-05-2022, 06:08 AM   #2
JWA
Senior Member
 
Join Date: Jan 2011
Location: Reynoldsburg, Ohio
Posts: 3,774
Send a message via Yahoo to JWA
As GFI's age or are repeatedly tripped they "wear down" and become less able to hold the circuit closed. It would be a best practice to match the GFI's amp rating to the breaker but it would be no issue if its of a lower rating.

HTH
JWA is offline   Reply With Quote
Old 05-05-2022, 08:55 AM   #3
Senior Member
 
Scalf77's Avatar
 
Join Date: May 2007
Location: Beaverton, OR
Posts: 2,506
If the breaker for the circuit is 15 amps the GFI should be 15 amp.

-greg
Scalf77 is online now   Reply With Quote
Old 05-05-2022, 09:33 AM   #4
Senior Member
 
Join Date: May 2018
Location: Arizona
Posts: 670
I did not know this
https://www.homelectrical.com/how-lo...ts-last.6.html
posplayr is offline   Reply With Quote
Old 05-05-2022, 09:51 AM   #5
Site Team
 
daveb's Avatar
 
Join Date: May 2007
Location: Turlock Ca
Posts: 10,409
Garage
Quote:
Originally Posted by rtamobile View Post
When we had a pre-purchase RV inspection done the GFI kept tripping. We were told to replace the old GFI with a new 20A GFI outlet, even though the GFI Breaker is only 15Amp. Help me understand that? Should the new GFI be only 15A - the same as the breaker or does it matter?
I wouldn't go higher amps unless I knew the wiring and electrical system is rated to handle the higher amps.
__________________
2006 Ford 6.0PSD EB-50/E-PH SMB 4X4 Rock Crawler Trailer

Sportsmobile 4X4 Adventures..........On and off road adventures
daveb is offline   Reply With Quote
Old 05-13-2022, 05:59 AM   #6
Junior Member
 
Join Date: Dec 2012
Posts: 19
I would suggest the circuit breaker is the over current protection device. The ampere rating of the GFI recep. indicates the current it can safely handle. The GFI recep is a safety device designed to trip when current leakage to ground exceeds some safe/trivial amount, it is not an overcurrent protective device. I agree with the statement that old GFI receps may tend to trip prematurely and should be replaced. While I don't know it to be a fact, it would not surprise me if a 20 amp GFI recep tolerates finitely higher ground fault leakage compared to a 15 amp model.
maurshir is offline   Reply With Quote
Old 05-13-2022, 07:34 AM   #7
Senior Member
 
Join Date: Aug 2019
Location: Elk Grove, CA
Posts: 391
Industrial and even hospital grade GCFIs are available. I don't know, but I would assume that they're more resistant to premature failure. I also agree that sticking with the same amp rating as your breaker is a good idea.

https://www.homedepot.com/s/industrial%2520gfci?NCNI-5
__________________
Bob
2005 E350 Super Duty Ext Wheelchair Van
2002 Itasca 35U Motorhome
BCam is offline   Reply With Quote
Old 05-13-2022, 08:06 AM   #8
Senior Member
 
wanderers's Avatar
 
Join Date: Jan 2016
Location: Southern Indiana
Posts: 125
Garage
A 20amp receptacle can accept a 20amp plug, which could overload the breaker, which is why the National Electrical code says you can't do it. I would stay with the 15 amp receptacle. If the new receptacle keeps tripping then there is probably a small leak of power between the conductors. Some GFIs do get weak and some are probably too sensitive from the start. I wouldn't put a 20amp in, even though I have never used any appliance with a 20a plug, and not many people have, it would still be best to stay with the correct receptacle. Since the receptacle is designed to trip with an imbalance of current on the conductors, increasing the load capacity of the receptacle shouldn't change whether or not you get nuisance tripping.
wanderers is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Sportsmobile SIP or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 01:40 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.