Old 03-14-2018, 11:42 AM   #11
Member
 
Join Date: Mar 2011
Location: San Diego
Posts: 96
Quote:
Originally Posted by i3enhamin View Post
Side notes...

I don't know why these guys are building giant aluminum radiators out of their water heaters. I WON'T be copying that for summer months.
Yeah, I have mine valved so it doesn't circulate through the air heating unit during the summer.

clark is offline   Reply With Quote
Old 03-14-2018, 11:51 AM   #12
Member
 
Join Date: Mar 2011
Location: San Diego
Posts: 96
My expansion tank is not inside the camper either...
clark is offline   Reply With Quote
Old 03-14-2018, 11:55 AM   #13
Junior Member
 
Join Date: Dec 2017
Posts: 20
My expansion tank will be under hood and I will have a 3-way summer valve, too.

I don't have the Rixen coolant tank... that functionality, for me, will be split across 2 components. I purchased this already and am looking at something like this for the AC heated / insulated buffer tank.
i3enhamin is offline   Reply With Quote
Old 03-14-2018, 11:57 AM   #14
Member
 
Join Date: Mar 2011
Location: San Diego
Posts: 96
Quote:
Originally Posted by i3enhamin View Post
One more instance...

This one you can clearly read is a 0.14m^2 Duda B3-14DW

Good enough for me! $66 on Amazon it looks like. I have an email out to the guy I bough my current heat exchanger from to make sure it's not my mixing valve that is the issue.
clark is offline   Reply With Quote
Old 03-14-2018, 11:59 AM   #15
Junior Member
 
Join Date: Dec 2017
Posts: 20
I'm not certain yet that that "point of use" water heater is totally legit for this application, but I don't see any reason why not yet. Seems the temperature and pressure relief are sufficiently high that it will just act like a more affordable insulated buffer tank.

My system is written up here fwiw.
i3enhamin is offline   Reply With Quote
Old 03-14-2018, 12:11 PM   #16
Member
 
Join Date: Mar 2011
Location: San Diego
Posts: 96
you running the coolant or the water through the buffer tank? Rixen doesn't have a pressure relief valve on the water side and the expansion take with the radiator type cap should act as a pressure relief for the coolant as well as letting air in/out as you go up or down in altitude.
clark is offline   Reply With Quote
Old 03-14-2018, 12:15 PM   #17
Junior Member
 
Join Date: Dec 2017
Posts: 20
I'm running coolant through the buffer tank. My expansion tank's 7-lb cap will appropriately make it act as the expansion tank. The 100-lb relief valve on the buffer tank should be moot given the difference. Any pressure vessel should still have a relief valve of some sort though, IMO... so, I think all is well.

I'm going for a very large coolant capacity to:
- Reduce cycling
- Provide lots of heat capacity for very long shower duration

And, I'm going with an adjustable electric heater so I can toggle back and forth between asking less of my batteries and asking more of shore power.

I might still be missing something, but if I am, I'm not seeing it.
i3enhamin is offline   Reply With Quote
Old 03-14-2018, 12:16 PM   #18
Junior Member
 
Join Date: Dec 2017
Posts: 20
Of course the expansion tank needs to be installed higher than the buffer tank... and everything else for that matter.
i3enhamin is offline   Reply With Quote
Old 03-14-2018, 12:20 PM   #19
Junior Member
 
Join Date: Dec 2017
Posts: 20
Fwiw... I'm a huge skeptic that a 17,000 btu / hr Espar D5 truly provides continuous on demand water.

Shower heat demand from the system:
1 gpm * 8.34 lbs / gallon * 50 deg F = 417 btu / min = 25020 btu / hr

Energy input into the system:
17000 btu / hr = 283 btu / min

I do not see how that can possibly provide continuous on-demand showers... hence the "shower-sized" coolant capacity. I figure a 7-gallon heater ~ a 6-gallon marine water heater sans heat exchanger coil.
i3enhamin is offline   Reply With Quote
Old 03-14-2018, 12:23 PM   #20
Junior Member
 
Join Date: Dec 2017
Posts: 20
And almost all shower heaters are more like 35,000 - 40,000 btu / hr... this seems to support my skepticism as well.

Ecco-temp L5

I'm happy to be convinced otherwise, but these are my calcs / understanding of the matter.
i3enhamin is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

» Sportsmobile Registry

2006 Ford E250

Lenny

At-At

Dirk/co
Add your Sportsmobile
» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Sportsmobile SIP or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 10:27 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.