Thanks for that, it was just what I needed. Capacitor was bad. Installed a replacement but am seeing the same behavior: there's a click, the compressor starts, then after a second or so there's another click and the compressor shuts off. The process repeats every 10-15 seconds.
The clicking is definitely the AC relay. I put the meter across the lower two terminals of the AC relay (see attached) and it reads 120V with the compressor off. As soon as the relay clicks, the meter drops to 100-105V and then the compressor shuts off and the meter returns to reading 120V.
Two other pieces of info:
1) The replacement capacitor is physically smaller than the original. I had a hard time finding an exact replacement but this one was smaller than I expected. Picture attached.
2) With the capacitor removed but without disconnecting any other wires, I checked for continuity across the various terminals of the relay and they all had continuity with each other. For example, with one lead on the upper right terminal, there was continuity with the other three. Same when testing upper left, lower right, lower left. That seems bad, but I wasn't sure since I didn't disconnect the wires. Can't find any info about the relay so not sure which terminals are the coil and which are the switch, or how to find a replacement.
|