For more clarity the BMS max discharge rate is 600 Amp for 4 seconds, they don't really list a nominal discharge current, but do list 200 amps as the max charge current. It would generally be safe to say the same value could be used for discharge current. Acopower's website is limited on specifications. If you ask for more it will just shutdown, not limit current as @1der says.
The BMS should be looked at as a safety device much like fuses and breakers, your goal is to design your system to not shut down the BMS in normal operation.
For the solar panel fusing, the critical specification aren't provided (ISC) or short circuit current and maximum series fusing rating. I would suspect that no fusing would be needed in a parallel or series setup. The 20 amp dual breaker is acting as a disconnect switch, as we should never really see 20 amps on that circuit.
The BMS should be looked at as a safety device much like fuses and breakers, your goal is to design your system to not shut down the BMS in normal operation.
For the solar panel fusing, the critical specification aren't provided (ISC) or short circuit current and maximum series fusing rating. I would suspect that no fusing would be needed in a parallel or series setup. The 20 amp dual breaker is acting as a disconnect switch, as we should never really see 20 amps on that circuit.